Short answer: Most of the time it is load: too many big appliances running at once for a 30 amp or 50 amp connection. The next most common causes are a worn pedestal breaker or receptacle on the park’s side, or a fault inside the RV. When it trips, and what was running, usually tells you which. An energy management system (EMS) takes the guessing out of it.

The parts involved

  • Pedestal breaker. The park’s breaker for your site. It trips when current goes over its rating, and older breakers that have tripped many times can wear out and trip early.
  • Pedestal receptacle and your shore power plug. The connection between the park and your RV. A worn or loose contact heats up under load; look for discoloration, melted plastic or a hot plug.
  • RV main breaker panel. Your own breakers. If an RV breaker trips first, the problem is inside the RV; if the pedestal trips first, it could be either side.
  • Converter or inverter/charger. Charges your batteries from shore power and adds to the load while it does.
  • EMS. Shows live voltage and amps on each leg, and checks the pedestal for wiring faults before your RV connects.

How much a pedestal can carry

ConnectionUsable powerRoughly what that runs
30 ampabout 3,600 wattsone rooftop A/C plus a few small loads
50 amptwo 50 amp legs, about 12,000 wattstwo A/Cs, the electric water heater and the microwave, if spread across both legs

Typical draws: a 13,500 BTU rooftop A/C uses about 1,300 to 1,600 watts while running, an electric water heater element about 1,400 watts, and a hair dryer about 1,500 watts. A standard RV microwave uses about 1,000 to 1,500 watts, but the large residential microwaves in many premium fifth wheels, Class As and Super Cs can pull as much as 2,400 watts. On a 30 amp site, the A/C, water heater and microwave together are already over the limit.

Reading the clues

  • It trips a few minutes after the microwave, hair dryer or a second A/C comes on. That is overload. Switch the water heater to propane, and stagger the big loads.
  • It trips the moment you plug in or switch the breaker on. That points to a short or a fault. Leave it off and have it diagnosed.
  • It trips on hot afternoons at loads that were fine in the morning. Park voltage often sags when every RV runs its A/C. Low voltage makes motors such as A/C compressors draw more current, and a tired breaker trips sooner when it is hot. Your EMS display will show the voltage.
  • It keeps tripping at your site. The problem is either that pedestal or your RV. If your cord reaches, plug into the neighboring pedestal with the same loads running. If that one trips too, the problem is in your RV. If it doesn’t, the problem is your site’s pedestal, so ask the park for maintenance or another site.
  • It only trips on the 20 amp outlet. Those outlets are GFCI protected and trip at about 5 milliamps of leakage. Small leakage from several RV appliances can add up past that without a single fault (RVtravel, Mike Sokol). Use the 30 or 50 amp outlet, and have us test if it still trips.
  • The plug or receptacle is hot, discolored or smells burnt. Stop using it. A failing connection is a fire risk, and the RV’s plug should be replaced.

What not to do

  • Don’t hold a breaker on or keep resetting it under load.
  • Don’t use an adapter to get around a GFCI outlet, and never remove a ground pin.
  • Don’t replace a breaker with a larger one. Breakers are sized to protect the wiring behind them. With a breaker rated higher than its wiring, a fault on that line can overheat the wire long before the breaker trips, and that is how RV electrical fires start.

If you have a Victron inverter/charger

Victron inverter/chargers let you set an AC input current limit to match the pedestal, so the RV never pulls more than the site can give. With PowerAssist turned on, the batteries cover short peaks above that limit, such as the microwave running with the A/C (Victron Energy). Set correctly, it is one of the most effective fixes for pedestal trips we know of. We set both up on every Victron system we install, and show you how to change the limit from the Victron Cerbo GX when you move between 30 and 50 amp sites.

Your EMS is the first tool

A good EMS checks the pedestal for reversed polarity, open ground or neutral and bad voltage before your RV connects, and shows live amps so you can see how close you are to the limit. See do I need a surge protector or an EMS for my RV?

How we diagnose it

We test the pedestal under load, inspect your shore power cord, plug and RV panel, measure what your appliances actually draw, and check for leakage and wiring faults inside the RV. You get a clear answer on whether the problem is the park’s equipment or your RV, and what it takes to fix it.

Common questions

Can I ask the park to fix the pedestal?

Yes. Your EMS readings or our test results give the park something specific to act on.

Will a 50-to-30 amp adapter cause trips?

The adapter doesn’t trip anything, but it limits a 50 amp RV to 30 amps on a single leg, so you have to run less at once.

Does a tripping breaker damage my RV?

The trip itself is the breaker doing its job. Repeated trips are a warning sign, and the low voltage that often comes with them is what damages appliances.

Find out if it’s the pedestal or your RV